Skip to content
Equinox
Search the Journal

The new heat pump had to use the old air paths

By Ben3 min read

The outdoor equipment in the proposal was new. Almost everything carrying air around our house was older than I was. I wanted to know how those two facts would work together.

A large return-air grille with clear space in front of it.
In this article

The back bedroom already received less useful airflow than the front room. I put that room on the site-visit list before asking which heat pump we should buy. Keeping the ducts could make sense, but their age and the fact that they had served a furnace did not settle it.

Ask what the existing ducts can deliver

Heat pumps often deliver a larger volume of air at a lower temperature than furnace heating. NRCan therefore recommends checking the existing distribution against the selected heat pump's airflow needs. The question is whether these ducts can carry the required air without excessive resistance or noise.

I asked for the assessment to cover the main supply and return routes, the branches serving difficult rooms, and accessible leaks, damage or insulation gaps. I described our closed bedroom doors, basement office and room above the extension. The assessment needed to reflect the rooms as we used them.

Ask for findings you can understand

The contractor's checks can include airflow and external static pressure: the pressure associated with moving air through the connected system. The readings need to be interpreted against the actual fan, filter, coil and manufacturer's limits. A pressure number without the operating conditions is not a pass or fail you can apply to a new heat pump.

  • What airflow does the proposed system require, and what does the assessment show the existing arrangement can deliver?
  • Which rooms or return paths need attention, and what evidence points to each problem?
  • What will be repaired or changed, and which concerns will remain?
  • How will airflow and operation be checked after the new equipment and any duct work are installed?

I wanted the installer to do the measurements. Feeling air at a grille could tell me where to describe a comfort problem; it could not establish the system's capacity.

Turn the findings into a scope

If the proposal says 'duct modifications as needed', ask what has already been identified and how additional work will be priced. List the intended changes to branches, returns, grilles or sealing, and whether opening and repairing ceilings or walls is included. Keep the assessment and final test records with the equipment documents.

An equipment upgrade should not quietly inherit an unresolved back-bedroom problem. I asked the contractor to show how the proposed work addressed that room, or to say clearly if it did not. That answer mattered more to us than how new the outdoor cabinet looked.